The Refrigerant Screw Compressor uses Castrol Icematic SW100 Oil as Lubricant. The Refrigerant is R134a. The Oil was tested due to frequent clogging of the Lube Oil Filter.
The Viscosity @40 found reduced from 100 to 60 cst and the pour point increased from -33Deg to -26DegC. Should the Oil be replaced or sweetening(bleed and feed) with 50% fresh oil will help? or additioal test is required? |
||
|
|
Double Platinum Member - 100 or more posts |
I dont think its possible for an ISO VG100 oil to reach 60 cSt/40degc, because it can not go under the syntetic base oils viscosity.
Its most likely a ISO 68 oil been used (Or a mix of ISO 100 and ie. ISO 32/46?) You need to stay within specification with the viscosity (check manual) to maintain lubrication and evt. sealing properties. If visc. (according to manual) is ok: I would recommend to check acid content (TAN). If TAN is high (over 0.2); change oil. ALso check moisture content. If the oil is soure (high TAN), it is not a good idea to fill up with new oil. A compete oil change is then required. This message has been edited. Last edited by: mr. Hughes, |
|||
|
|
Bronze Member - 1 or more posts |
Be sure to let all the refrigerant degas before testing the viscosity. This is a common observation in refrigeration. A small amout of refrigerant can make the oil appear to be way of specification so far as viscosity at 40C.
Having said that - to make the oil mentioned drop to 60 cSt when running a standard kinematic viscosity, it would take more refrigerant than is likely to remain disolved once set out in a sample bottle. By the way - POEs can degrade to lower viscosity. But I can't say that I have ever seen one do that so drasitcally in an HFC application - and as was mentioned, we woudl expect to see a high acid number in that event. |
|||
|
|
Platinum Member - 50 or more posts |
Joy,BVA(Dave?) - I would worry about two things with the problem you have described. The plugging of the filters is a serious issue that suggests major problems in the compressor or system.
Excessive heat at a metal wear surface can decompose the POE and can cause the viscosity to drop. Thermal decomposition can result in cracking off small molecular weight fragments from the acid chains, and can best be seen by analyzing the refrigerant looking for the presence of small MW hydrocarbons. You may also find high amounts of wear metals in the POE from the metal - metal contact. The TAN number does not always go up a lot due to thermal breakdown. The filter plugging may be wear debris. If the POE decomposition is due to moisture (hydrolysis), then carboxylic acid salts may be the source of the filter plugging. The viscosity will generally drop as a result of hydroysis as well. The salts are generally wax-like semi-solids. The TAN number will generally rise quite a bit to the 0.2 limit or higher. You may also see corrosion metals in the POE sample as the water and acids go to work on the system. The absence of any decomposition products coupled with a viscosity drop is either from improper refrigerant stripping prior to testing the viscosity, or the addition of a lower viscosity POE to the compressor. Infrared anaysis of the POE is a good tool to see if the POE is mixed. You can also see large refrigerant bands in the infrared spectrum if the sample contains more than about 1% residual refrigerant. Since you have filter plugging, I would not suspect POE mixing or dilution to be the problem. Bottom line: if the filter is plugging, then change out the POE lube. The breakdown of POEs are autocatalytic, which means the presence of POE breakdown products results in faster decomposition of the remaining POE. Add filter dryers to help remove any acidity to keep the system clean as long as possible. This message has been edited. Last edited by: refrig guy, |
|||
|