We operated our DEH control fluid temperature at about 170 degrees Fahrenheit for about three hours due to a loss of cooling water. We have a 1300 mw unit, with Fyrquel as the control fluid. Do you have any comments or experience with this? We sent a smaple to the Supresta lab and it indicated okay. Thanks!
While the fluid might test okay Supresta do not do some of the more useful tests like color. If the fluid was overheated just because the coolers were out of service or something else that caused bulk overheating, then it should be fine. If it was overheated because you ran both pumps for some time and the compensators were set wrong so that the excess fluid was discharging through a pressure relief valve back to the reservoir, then the compression of entrained air could burn the fluid. Depending n the cause you might ask them to start doing color. New fluid is less than 1 while normal fluid in service is a 2-3 on the ASTM Scale. While the scale is for mineral oil and phosphate esters do not go through a red phase, it is helpful. A 7-8 is not good but still workable depending on the system. Some NEIP and ABB systems tend to darken the fluid.