If the refrigerant was completely removed from the Trane 22 prior to testing for viscosity, and you got only 28 cSt, then it is likely mixed. The Trane compressors do not normally shear the oil, and if it were under that much stress there would be signs of other major problems in the oil analysis (high acidity, very dark color, high levels of wear metals etc.) If you have any more information that supports severe chemical degradation of the oil, then the oil may have been chopped up to lower viscosity.
I still have doubts about the test lab's removal of dissolved refrigerant prior to viscosity testing. Trane 22 is used with one of three refrigerants (R-11, R-22 and R-123). R-11 and R-123 are very difficult to remove from the oil since they have lower volatility than most other refrigerants. R-22 is fairly easily removed compared to the other two refrigerants.
FTIR can be used to tell if there are significant amounts of dissolved refrigerant.