I am new to a hydro plant that has lost documentation of it's turbine oils. Without knowing the oils manufacturer and weight I have nothing to compare to and need do get a baseline.

Our samples are comming back saying the oil is fine but no explanations of the numbers.

Last week I did the first acid test and it came back as .10, anyone know if this is good or bad?
Original Post

Replies sorted oldest to newest

I would claim that TAN value of 0.10 is just fine (Depending on oil type of course). I have a reference sample from Regal oil R&O 68 giving 0.07 (after ASTM D-664).

Note: TAN does not always give good enough confirmation of oxidation problems in turbine oils. You should look into FT-IR analysis (peaks at 1630 & 1714 cm-1), Gravimetric analysis and Ultracentrifuge test (RPVOT). Also regular particle counts are recommended.
quote:
Originally posted by mr. Hughes:
Note: TAN does not always give good enough confirmation of oxidation problems in turbine oils. You should look into FT-IR analysis (peaks at 1630 & 1714 cm-1), Gravimetric analysis and Ultracentrifuge test (RPVOT). Also regular particle counts are recommended.


Just for clarification to readers, RPVOT is not and never has been the "Ultracentrifuge test", as could be easily miss-understood from the above quote.
I agree, we use a General Guideline of 0.10 for unknown turbine oils and unknown OEM (why do people send in samples with no info and data???) Anyway, look for a doubling of that TAN value to 0.20 as a critcal limit, again,this a GENERAL GUIDELINE. And remember,that the TAN test has accuracy and repeatability issues at this low level (makes it even more fun) so, you would be best to back up the TAN with a RULER and FTIR tests.